    Quote Originally Posted by offtohavasu View Post
    Can you do a quick test? Where the wire comes out of the breaker at the pedestal, put the clamp meter there and note the amps (with all your loads). Then put the clamp on the neutral and measure the amps and report back please.
    Hi Curtis,

    I could have done that yesterday when we had the panel open, but it’s too busy today to do it with the park personnel. BUT, I have a neighbor who has a clamp Meter, and I can do it myself if it’s worthwhile. Can you tell me what we’re looking for or what we’ll accomplish by doing this test so I can decide whether to do it without an employee?

    Steve
    Steve & Sue (pups:Sky & Sierra) Gardnerville, Nv
    2017 Refelection 297RSTS
    2017 Ford 350 CC 4x4 Lariat Superduty 6.7, Long Bed

  2. #52
    Long Hauler offtohavasu's Avatar
    Join Date
    Dec 2014
    Location
    Fountain Valley, CA
    Posts
    2,254
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I want to see what the actual amperage is at the breaker and what is being returned on neutral
    Curtis, Christine, Cole, and Charlotte

    2007 Chevrolet Silverado Duramax LBZ, CCLB
    2020 Momentum 351M

  3. #53
    Big Traveler Steve7's Avatar
    Join Date
    May 2016
    Location
    Gardnerville, Nv
    Posts
    1,627
    Mentioned
    5 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by offtohavasu View Post
    I want to see what the actual amperage is at the breaker and what is being returned on neutral
    Yeah, I figured that, but if it’s not what it should be, what does that tell us?
    Steve & Sue (pups:Sky & Sierra) Gardnerville, Nv
    2017 Refelection 297RSTS
    2017 Ford 350 CC 4x4 Lariat Superduty 6.7, Long Bed

  4. #54
    Seasoned Camper acadiaforever's Avatar
    Join Date
    Sep 2017
    Location
    Bass Harbor, ME
    Posts
    353
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If the neutral current is less than the hot current, it would mean that you have a leak to ground. If you can read it on the resolution of a clamp meter in the 40A range, it would be a SERIOUS leak to ground. For even small leaks to ground, your EMS should have shut you down.
    Al and Kathe
    House: Bass Harbor, Maine
    Home: Wherever we're parked
    [SIGPIC][/SIGPIC]
    Highlighted states are those we have camped in for at least one night in our Solitude.
    2018 Solitude 310GK 110463 (Rhett) / 2018 F350 CC DRW 4x4 Lariat (Scarlett)
    Follow us: http://lobstersontheloose.com

  5. #55
    Big Traveler Steve7's Avatar
    Join Date
    May 2016
    Location
    Gardnerville, Nv
    Posts
    1,627
    Mentioned
    5 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by acadiaforever View Post
    If the neutral current is less than the hot current, it would mean that you have a leak to ground. If you can read it on the resolution of a clamp meter in the 40A range, it would be a SERIOUS leak to ground. For even small leaks to ground, your EMS should have shut you down.
    Got it Al, thanks. If I get the opportunity, I’ll check it tomorrow morning.
    Steve & Sue (pups:Sky & Sierra) Gardnerville, Nv
    2017 Refelection 297RSTS
    2017 Ford 350 CC 4x4 Lariat Superduty 6.7, Long Bed

  6. #56
    Long Hauler offtohavasu's Avatar
    Join Date
    Dec 2014
    Location
    Fountain Valley, CA
    Posts
    2,254
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Thanks Al.
    Curtis, Christine, Cole, and Charlotte

    2007 Chevrolet Silverado Duramax LBZ, CCLB
    2020 Momentum 351M

  7. #57
    Rolling Along carnolddsm's Avatar
    Join Date
    Jul 2015
    Location
    Quartzsite until April
    Posts
    577
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by acadiaforever View Post
    If the neutral current is less than the hot current, it would mean that you have a leak to ground. If you can read it on the resolution of a clamp meter in the 40A range, it would be a SERIOUS leak to ground. For even small leaks to ground, your EMS should have shut you down.
    Not necessarily, on 50 amps the two hot legs are supposed to be 180 degrees out of phase with each other. The neutral in these systems only carries the difference in loads of each leg. Example: leg black is passing 20 amps, leg red is passing 5 amps, the current on the neutral is 15 amps (20 - 5).

    The two hot legs cancelling each other allows the neutral wire to be sized the same as the hot legs. If this were not the case on a 50 amp RV cord the neutral conductor would have to be significantly larger.

    The reason for saying the two hot legs are “supposed” to be 180 degrees apart is I’ve seen reports of RV parks being incorrectly wire with both hot legs in phase. This can cause a serious overloading of the neutral wiring.
    Last edited by carnolddsm; 05-25-2019 at 10:00 PM.
    Colan and Marilyn Arnold
    Des Moines, IA - kind of, on the road full time.
    Currently in Durango, Colorado
    Momentum 350M originally, now a 397TH

  8. #58
    Site Sponsor Jerryr's Avatar
    Join Date
    Nov 2016
    Location
    Florida
    Posts
    2,822
    Mentioned
    30 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by carnolddsm View Post
    Not necessarily, on 50 amps the two hot legs are supposed to be 180 degrees out of phase with each other. The neutral in these systems only carries the difference in loads of each leg. Example: leg black is passing 20 amps, leg red is passing 5 amps, the current on the neutral is 15 amps (20 - 5).

    The two hot legs cancelling each other allows the neutral wire to be sized the same as the hot legs. If this were not the case on a 50 amp RV cord the neutral conductor would have to be significantly larger.
    That’s true with a 50 amp 240 v service. What was asked was to measure hot current and neutral current at the pedestal 30 amp 120 v single pole breaker that supplying power to the trailer.
    Jerry & Linda
    Emma & Abby our Mini Golden Doodles & JR our Amazon Parrot
    2017 Reflection 337RLS, Build Date 01/2017, Titan Disk Brakes, Goodyear G614s 235/85/16 G Rated tires
    2022 F-450 King Ranch Ultimate, 4,868 lb Payload, Bedrug Bedliner, Andersen Ultimate II Aluminum 5th wheel hitch
    http://visitedstatesmap.com/image/FLGANCSCsm.jpg

  9. #59
    Long Hauler offtohavasu's Avatar
    Join Date
    Dec 2014
    Location
    Fountain Valley, CA
    Posts
    2,254
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    If the neutral is not matching the output, that is going help to start diagnosing issues.
    Curtis, Christine, Cole, and Charlotte

    2007 Chevrolet Silverado Duramax LBZ, CCLB
    2020 Momentum 351M

  10. #60
    Rolling Along carnolddsm's Avatar
    Join Date
    Jul 2015
    Location
    Quartzsite until April
    Posts
    577
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jerryr View Post
    That’s true with a 50 amp 240 v service. What was asked was to measure hot current and neutral current at the pedestal 30 amp 120 v single pole breaker that supplying power to the trailer.
    My apology, I missed that.
    Colan and Marilyn Arnold
    Des Moines, IA - kind of, on the road full time.
    Currently in Durango, Colorado
    Momentum 350M originally, now a 397TH

Page 6 of 7 FirstFirst ... 4567 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.