I had a welding outlet in my shop and replaced it with a 4 prong 50 amp rv plug. I found a 50 amp to 3 prong welding plug adapter so I can still use my welder when needed.
-
04-01-2021, 04:39 AM #33
- Join Date
- Jun 2020
- Posts
- 162
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
We recently (earlier this week) ran into the exact same issue. What we did was build an adapter cable assembly with the 3 prong on one end, and 4 prong 50A female on the other. The standard 3 prong connection is used: hot 1 to hot 1, hot 2 to hot 2, and neutral to neutral.
On the 4 prong end, install a jumper wire between the ground and neutral connections, effectively shorting the neutral to ground. Make sure it's heavy enough gauge to handle 30A of current. Without connecting to your EMS, measure across the 2 hot leads. You should get around 230VAC. measuring from either hot lead to ground and/or neutral should yield about 120VAC. Again, do this before connecting to your EMS!
If it measures correctly, connect only to your EMS. You should get the required readings, and no errors on your EMS, and should be save to use.
Disclaimer: this method worked for us, but may not work for you. YMMV. If in doubt, call an electrician.
-
04-01-2021, 05:35 AM #34
- Join Date
- Mar 2021
- Posts
- 585
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
-
04-01-2021, 06:16 AM #35
- Join Date
- Mar 2020
- Location
- Whatever state the landing gear sits upon (Texas c
- Posts
- 763
- Mentioned
- 16 Post(s)
- Tagged
- 0 Thread(s)
I understand that, but I was under impression Watchdog caught the single phase as it monitors both legs and would see the voltage exceed 134 overall. I guess it only monitors each leg and doesn't look for split phase vs single phase set ups.
Sent from my SM-N986U using Tapatalk
-
04-01-2021, 07:02 AM #36
- Join Date
- Feb 2019
- Location
- "Murvul", TN
- Posts
- 3,449
- Mentioned
- 138 Post(s)
- Tagged
- 0 Thread(s)
Unless you rewired the wiring coming to the welder recept to have 4 wires instead of three, you are using the ground wire as a neutral.....which is completely against electrical code and is a very dangerous way of doing things. The ground conductor....which is what the original recept had (two hot leads and a ground) should NEVER BE a current carrying conductor. It's only purpose is for providing a path of current flow in case of an electrical fault.
2016 F350 CrewCab Dually
2018 Momentum 394M...Heavily Modded!
2023 Suzuki GSX-S1000 GT+
Excessive Payload is a Wonderful Thing
"If it ain't fast....It ain't Fun"
-
04-01-2021, 10:07 AM #37
- Join Date
- Jul 2017
- Location
- SW Indiana
- Posts
- 1,985
- Mentioned
- 42 Post(s)
- Tagged
- 0 Thread(s)
The voltage between the hots on any electrical service is always 240V unless an RV pedestal or adapter is feeding both legs of the RV from a single hot, then it would be zero. You will never see any other voltage between hots barring an electrical service problem. 50A RV service is 240V, so the EMS isn’t going to alarm because of that. 120V is only available from either of the hots to neutral or ground, and that measurement is what an EMS looks at. Since neutral and ground are connected to the transformer center tap, they are always 120V from either hot.
John & Kathy
2014 F250 Lariat FX4 6.2L SBCC
2014 Reflection 303RLS
SW Indiana
-
04-01-2021, 10:38 AM #38
- Join Date
- Aug 2019
- Posts
- 162
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
The plug was right next to the breaker. I had room for two 120v breakers and it already had a neutral and ground wire there so re-wiring was easy.
I didn’t add a 50 amp plug and keep the 220v welder plug because I did not have room to add the breakers.
So I made it work rather than buy a whole new box.
-
04-02-2021, 10:22 AM #39
- Join Date
- Apr 2020
- Posts
- 231
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
OK, so the Watchdog EPO (aka EMS) should (is designed to) catch a fault if it occurs from the Ground to Neutral wiring..?
And yes, I understand this re-wiring is not ideal ,and is not to "Code"; but I have only 3 weeks left at this location, and if the Watchdog EPO/EMS will do its job until then and keep me and my electronics safe, then perhaps this is the workaround that works best for my situation right now..?
-
04-02-2021, 11:03 AM #40
- Join Date
- Feb 2019
- Location
- "Murvul", TN
- Posts
- 3,449
- Mentioned
- 138 Post(s)
- Tagged
- 0 Thread(s)
I'm going to muddy up the water a bit here. I have never personally seen this, but I wasn't necessarily looking for it either. I've heard this for the last couple of years, that there are RV parks (newer ones being built) that are now using 208 3phase Wye from the transformers that provide power to the pedestals at their campgrounds. Has anyone here....who actually knows what I'm talking about, seen that scenario? On that power pedestal, you would read the following voltages. L1 to neutral 120VAC, L2 to neutral 120VAC and then from L1 to L2 the reading would be 208. Anyone seen it out there. Most folks wouldn't ever notice it unless they use a meter and test voltage before they plug into the pedestal power, and got 208 instead of the more normal voltages seen with a Split phase system of 230-240V
2016 F350 CrewCab Dually
2018 Momentum 394M...Heavily Modded!
2023 Suzuki GSX-S1000 GT+
Excessive Payload is a Wonderful Thing
"If it ain't fast....It ain't Fun"
What changed for the new GD...
Today, 03:31 PM in General Discussion