    Using an EMS on Two Champion Generators and a Parallel Kit

    I know this topic has been covered before, but this is specific to the Champion 2000 watt inverter generators and matching parallel kit. If you attempt to run this combination through your Electrical Management System (EMS), you will get a fault (E2 on my Progressive Industries EMS) stating "Open Neutral". This happens because the ground and neutral are not tied together at any point in the circuit like it would be from shore power. In my case, the EMS will not turn on and allow power to pass through because of the error.



    It is very easy and inexpensive to resolve this issue on your own. Purchase a male extension cord repair plug. Insert a short length of AWG 12 or AWG 14 wire between the ground (Green Screw) plug and neutral (Silver Screw) plug. Make sure all screws are tightened and install the cover on the plug. This is now called a "Bonding Plug". See the photo below.



    Plug the bonding plug into any of the duplex outlets on either one of the generators as shown below.



    Voila - you now have ground and neutral tied together (Bonded) and your EMS will allow current to pass through to your RV. In the photo below, you'll see the EMS is now showing EO which means normal operation and the EMS turned on.



    Total Cost - $3.82 for the plug, and a piece of scrap wire I had laying in the garage.

    Jim

  2. #2
    Seasoned Camper bogen2's Avatar
    Join Date
    Mar 2018
    Location
    Edmonton, Canada
    Posts
    143
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I did this on my Champion 3200 and it works as Jim described. Simple easy fix so you don’t have to bypass the EMS. I use the same plug on my inverter to get it to work with the EMS too.

    Bob
    2014 Ford F-150 Ecoboost / Max Tow / HD Payload
    2018 Reflection 295RL

  3. #3
    King Pin
    Join Date
    Feb 2014
    Posts
    6,521
    Blog Entries
    10
    Mentioned
    41 Post(s)
    Tagged
    1 Thread(s)
    Great idea on the inverter Bob. Thanks!

    Jim

  4. #4
    Fireside Member HawgWild's Avatar
    Join Date
    Nov 2017
    Location
    Brea, CA
    Posts
    53
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Tucson Jim,
    Wife and I just bought a 337 Reflection and updgraded our truck (and trailer, Imagine 2950RL) to an F-350. I am looking at two Champion 2000 watt inverter generators with parallel kit for our Reflection so your posting on this topic is greatly appreciated! As always, I'm learning so much from your knowledge and postings. Thank you! - Rick
    Rick & B
    2018 Ford F-350 Lariat 4x4 6.7L, LB, SRW
    2019 Reflection 337RLS Fifth Wheel
    Pullrite Superlite 20K

  5. #5
    Fireside Member
    Join Date
    Aug 2018
    Location
    On the road (no home)
    Posts
    71
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the info on the champian gen. I just got a 3000w. Didn't know there was a problem. I will follow you advise.

    Thanks
    Otto
    Otto @ Susan
    2017 Dodge Ram 2500 diesel
    2018 Imagine 2600RB

  6. #6
    Site Sponsor
    Join Date
    Dec 2018
    Location
    Kenosha, WI
    Posts
    25
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This forum is amazing. Today I was pretty bummed out. Connected my two Champion 2000's with the parallel kit and connected to my 337. No power getting into RV & Progressive EMS says grounding error. I do a search here and the first thing that pops up is my exact problem follwed by the solution. Amazing. Wish there was a forum just like this one but called "Life Forum".
    Pete & Joyce
    2019 Reflection 337 RLS
    2019 F-350 6.7 Diesel Srw 4x4 CC Short Bed
    Andersen Ultimate Hitch

  7. #7
    King Pin
    Join Date
    Feb 2014
    Posts
    6,521
    Blog Entries
    10
    Mentioned
    41 Post(s)
    Tagged
    1 Thread(s)
    Glad to hear it worked for you Pete!

    Jim

  8. #8
    Setting Up Camp
    Join Date
    Apr 2019
    Location
    Waynesville, NC
    Posts
    16
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Will this also work on Wen gens? Having identical problem. thanks

    Sent from my Pixel 2 using Tapatalk

  9. #9
    Left The Driveway
    Join Date
    Aug 2018
    Location
    Columbia, SC
    Posts
    13
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IIRC bonding the neutral to ground is part of the chain of events that leads to "hot skin" condition that is so deadly

  10. #10
    Seasoned Camper
    Join Date
    Feb 2015
    Location
    Pasco, Wa.
    Posts
    317
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I don't think so in this case since there is no actual "ground" connection. This is just to trick the EMS.

    Safe Travels.

    Jim
    Jim & Gwen
    2015 Solitude 379fl, VIN 573FS4324F1102454
    2011 F-350 SC, DRW, 6.7 PSD, Ride-Rite Air Bags, Pull-Rite 20.5 K
    "You can't get lost if you don't care where you're going"

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.