    Generator back to Shore Power

    Newbie here.... We took our 21g out this weekend for the first time. Ran on Shore power all weekend. Before we left I wanted to get the generator running for a few minutes. I disconnected from shore before starting the generator from inside the rig. Turned it off from inside as well before we pulled away. Once we got home, I went to plug into the 110 to keep it plugged in while stored and it kept blowing the GFI on the plug.

  2. #2
    Site Sponsor
    Join Date
    Jul 2017
    Location
    SW Indiana
    Posts
    1,956
    Mentioned
    42 Post(s)
    Tagged
    0 Thread(s)
    Have you ever had it plugged into a GFCI protected outlet before? Some units have improperly wired transfer switches which create a ground-neutral bond within the trailer that causes a GFCI to trip.
    John & Kathy
    2014 F250 Lariat FX4 6.2L SBCC
    2014 Reflection 303RLS
    SW Indiana

  3. #3
    Left The Driveway
    Join Date
    Sep 2020
    Location
    Amarillo
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes sir.. been hooked to that same plug until we pulled out to go this weekend....Pulled back in and keeps tripping the same plug now... Another camper next to me is fine

  4. #4
    Paid my dues 😁 FT4NOW's Avatar
    Join Date
    Sep 2016
    Posts
    4,570
    Mentioned
    136 Post(s)
    Tagged
    0 Thread(s)
    Its possible the transfer switch is sticking. If you pop the cover off you can see if the contacts are open or shut for both sides.

    Sent from my SM-G950U using Tapatalk
    2023 Momentum 398M-R
    2023 Ford F-450

    SOLD - 2021 Reflection 311BHS
    SOLD - 2017 Momentum 399TH

  5. #5
    Left The Driveway
    Join Date
    Sep 2020
    Location
    Amarillo
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Dealer told me to make sure EVERYTHING was turned off before shutting the generator down. I went back out and started the generator up. Made sure everything was off. Let the generator run for a bit before shutting back down again. Then hooked back to shore and all was good.

  6. #6
    Seasoned Camper
    Join Date
    Oct 2016
    Posts
    317
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Not related to your GFCI problem but make sure you either run your generator out of gas by shutting off the fuel pump or drain the carb of gas. If not you may need to get a new carb down the road a bit. If you run your generator on propane disregard this post.
    Steve
    2017 F350 6.7 Lariat DRW
    2017 Momentum 388M
    North of Houston

  7. #7
    Left The Driveway
    Join Date
    Sep 2020
    Location
    Amarillo
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    will do THX!