Progressive Hardwired EMS 50 Amp / HW50C - High Frequency Error
I am having issues with my 2019 351M and a Progressive EMS unit. I get a high frequency error roughly 7/10 times when the automatic transfer switch first energizes and the contactors slam home. It does this on different power sources and with all DC disconnected and main breakers off. Progressive sent me a new unit, and it still does the same thing.
No issues once it either resets or I get one of the 3 times it does not trip. I have concluded that it has to be the transfer switch, but I have talked to Southwire / SureGuard 3 times, and they insist that it cannot be.
However, that is the only thing that gets power when it trips (when I have everything else disconnected). Also, the switch buzzes, and Southwire said that is normal because the relay vibrates. Well...Wouldn't this vibration potentially cause a frequency variation???
Any ideas??? Any help would be appreciated.
As a side note, my 351M has the SureGuard ATS model 40140 - specially designed for Grand Design. It is a cheaper version of their most basic ATS that GD specially requested. Nice.
-
11-19-2020, 10:12 PM #2
- Join Date
- Sep 2018
- Location
- Washington state
- Posts
- 512
- Mentioned
- 7 Post(s)
- Tagged
- 0 Thread(s)
Transfer switch buzzing should be from the AC cycle and therefore at the same frequency.
The DC side of things is separated by the converter, so shouldn't have any influence either.
Line frequency is set by the generators massive rotors. Not likely to shift!
Have a good long chat with Progressive!Rick
2019 Reflection 150 273MK
2015 Ford F350 CC SB Lariat Powerstroke
PullRite Superglide
-
11-20-2020, 07:20 AM #3
- Join Date
- Nov 2017
- Location
- Toronto, Canada
- Posts
- 1,974
- Mentioned
- 54 Post(s)
- Tagged
- 0 Thread(s)
Your post is thorough except that other than "different power sources" you don't mention the sources. Is this happening on shore power, generator power, or either?
When our generator was propane-fuel-starved and barely running the HW50C EMS was shutting down due to a high frequency error. (When we figured out the fuel problem the EMS was happy.) Long shot, but I thought I'd toss it in. Hope you get better ideas.
Good luck.Mark - 2018 Solitude 310GK - 2017 F-350 diesel SRW short box - Pullrite Superglide hitch
-
11-20-2020, 07:46 AM #4
- Join Date
- Aug 2018
- Posts
- 62
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
-
11-23-2020, 07:28 PM #5
- Join Date
- Aug 2018
- Posts
- 62
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
UPDATE: I spent some time and bypassed the ATS and found that the Progressive EMS worked fine. I went ahead and ordered a new Southwire / Sureguard ATS model 40100 and just installed it today. Success. All is working as it should.