In the furnace the flame at the base is blue but turns to orange everywhere else on the burner surface. Flame is blue in the gas stove, the water heater, and fridge. Yes, I did bypass the thermostat when bench testing it (just in case I also replaced the thermostat prior to that).
-
01-16-2021, 07:42 AM #12
- Join Date
- Oct 2020
- Location
- Virginia....up in the northern neck
- Posts
- 98
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
2021 GD Reflection 303rls
2019 ram 2500 Crew Cab tradesman 4x4
Autoslider 5th wheel hitch.
-
01-16-2021, 07:44 AM #13
- Join Date
- Jul 2020
- Location
- AZ
- Posts
- 34
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
-
01-16-2021, 07:47 AM #14
- Join Date
- Oct 2020
- Location
- Virginia....up in the northern neck
- Posts
- 98
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
I think low pressure would...wont force the exhaust gas out fully....but i am not sure. My first thought would be that it would build up soot which would retain heat....
Sent from my VS988 using Tapatalk2021 GD Reflection 303rls
2019 ram 2500 Crew Cab tradesman 4x4
Autoslider 5th wheel hitch.
-
01-16-2021, 07:53 AM #15
- Join Date
- Jul 2020
- Location
- AZ
- Posts
- 34
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
The only thing that hasn't been replaced is the gas line between the furnace to the first junction where it splits into three (furnace, water heater, main line). AirExcel and Grand Design are out of ideas and at this point concluded that this is normal. I don't think it is and I'm looking for Imagine 23BHE/21BHE owners who I could share with me how their furnace runs.
-
01-16-2021, 08:48 AM #16
- Join Date
- Oct 2018
- Location
- Cooksville, MD
- Posts
- 137
- Mentioned
- 3 Post(s)
- Tagged
- 0 Thread(s)
Can you hook the furnace up to another gas line (obviously after the regulator) to test it. Actually I would replace the regulator first and see if the problem still exists, then replace the gas line to the furnace. This should not cost very much to do.
The gas line may have in internal restriction or the regulator may be faulty - can you check the gas pressure with a manometer?
https://www.amazon.com/Manometer-RIS...0811937&sr=8-3
-
01-16-2021, 09:03 AM #17
If I understand correctly, you bench tested the unit(s) with the same short cycle result. Bench 12V, bench propane and bench thermostat or equivalent call for heat. If all this is true, why would the operation be any different in the rig? You know the power is good regardless of what the rig power is like and you know the propane supply is good regardless of any rig issues (good to know all other rig propane appliances working well) and you know the rig thermostat is good as it, like the power and propane supply, was not part of the bench test.
Although not what you or the service techs were expecting perhaps the units are now designed to operate this way. The only other consideration is the batch of units all have the same faulty part from the factory, hence your replacement operated same as the original.Judy & Larry
Ty and Ali the St Bernard drool machines
Delta, British Columbia, GWN
2019 Imagine 2150RB - lovingly christened “IM-A-GENE” towed by Dusty via Andersen 3350.
2018 F150 SCREW 3.5 EcoBoost Lariat - respectfully christened “Dusty”.
-
01-16-2021, 11:47 AM #18
- Join Date
- Jul 2020
- Location
- AZ
- Posts
- 34
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
-
01-16-2021, 11:53 AM #19
- Join Date
- Oct 2018
- Location
- Cooksville, MD
- Posts
- 137
- Mentioned
- 3 Post(s)
- Tagged
- 0 Thread(s)
Is 11 WC static or when the furnace is operating? Still could be a restriction somewhere that allows full pressure when static, but reduces when drawing a large quantity of LP.
-
01-16-2021, 11:54 AM #20
- Join Date
- Jul 2020
- Location
- AZ
- Posts
- 34
- Mentioned
- 0 Post(s)
- Tagged
- 0 Thread(s)
Very interesting about the same problem due to the same batch. However, mine was 2516 and the one I received is 2516A so I would guess it is a different batch.
The bench test intended to eliminate airflow restriction occurring in the ductwork which is the most common reason for overheating. We also bypassed the thermostat.