    Electricians please - Brand new RV AC / Voltage issues - Part 2

    Posted earlier as to my new Reflection 150 295RL fiver AC units not working well on 30A shore power at my home after working flawlessly at the 50A shore power at the dealer during the inspection. Voltage at the house pedestal was 117-118VAC - distance from the panel is roughly 175' or more. I helped pull the wire - it seemed pretty beefy but no clue as to how large the gauge was.

    Internal RV outlets on no-load were 114-116VAC. Main AC would kick in but immediately start "grunting" and outlets now read at 108-114VAC; bedroom AC would run 20-30 seconds and then trip the breaker. Checked with 50A cord with a dogbone adapter and a 30A cord with a locking adapter - all the same results.

    My Champion 3500 inverter genny finally arrived - put it in service and connected it to the RV with the same 30A cord. Got uniform 120-121VAC at the outlets. Both AC units cooled immediately upon setting the thermostat appropriately. (did not try to run both at same time as I don't have Easy Starts yet.) I could not identify any other electrical issues.

    Finally ordered a Progressive Industries 30A Outlet Tester - at the pedestal the red lights lit and read "Reverse Wiring" above and "Hot" and "Neutral" below. I assume this is what they call "reverse polarity?"

    First question: Could this "reverse wiring" be the sole cause for the issues I encountered?
    Next question: Is this something a handyman can rectify? or do you need a professional?

    Or am I totally off base and a completely different issue is ongoing at the pedestal? How would I diagnose it? I'd really like to have reliable shore power at my house in case we ever need to live/sleep in it someday.

    Thanks for any help.
    Ram 2500 Hemi V8 6.4L Long Bed
    2021 Reflection 150 295RL

    "If you're going to shoot, SHOOT. Don't talk."

  2. #2
    Site Sponsor
    Join Date
    Jul 2017
    Location
    SW Indiana
    Posts
    2,078
    Mentioned
    46 Post(s)
    Tagged
    0 Thread(s)
    Too much voltage drop. You can damage the air conditioners running on low voltage.
    John & Kathy
    2014 F250 Lariat FX4 6.2L SBCC
    2014 Reflection 303RLS
    SW Indiana

  3. #3
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,704
    Mentioned
    144 Post(s)
    Tagged
    0 Thread(s)
    117-118 VAC at the panel is considered a bit low. Most newer residences will see voltages in the 123-125VAC range, and of course on high electrical demand (think summer A/C units running by everyone that is on that transformer feed, can suck the voltage down considerably. On top of the "lower voltage" numbers at the house pedestal, you are using a 175' of some type of wiring to the RV. There will be additional voltage drop associated with that length of the circuit. It's likely that if you test the voltage at the end of the 175' run and do not have it connected to anything, thus NOT pulling a load on it, it will read very similar to the voltage at the house pedestal. Voltage drop occurs when a load is placed on the wires that feed the load. If you were to hook up the trailer and turn an A/C unit on you would likely see that the voltage at the breaker panel in the trailer is now maybe 8-10 volts less.

    In my opinion, you have two different issues that are affecting you. 1. The no load voltage at the house panel. 2. The length of the run feeding the trailer is likely not sized correctly for that distance and is causing some voltage drop. You said that you didn't know what size those wires were, so that is still an unknown at this point in time. Other possibilities include loose connections anywhere along the path to your RV....including at the house breaker panel, any terminations from there to the receptacle that you are plugging the trailer into, as well as possibly in the trailer itself.....although you did say that it performed OK when at the dealership's 50A shore power plug.

    The revers polarity indication needs to be corrected.....and if you have no real working knowledge or skills with electrical equipment, I would suggest hiring an Electrician that does. It is possible for the wiring to be reversed at the home breaker panel or at the 30A outlet that you plug into or any other terminations that might be in between those locations....if there are any. The bottom line though, it needs to be corrected. I don't believe that issue is causing the lower voltage issues you are experiencing, and I did state my thoughts about the why of the lower than normal voltage readings.....so basically, I would focus on finding out and fixing the reverse wiring issue, then the size of the 175' of wire feeding the trailer plug, and if necessary, you may have to replace that 175' run with a larger ga. wiring.
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

  4. #4
    Long Hauler geotex1's Avatar
    Join Date
    Sep 2019
    Posts
    2,888
    Mentioned
    84 Post(s)
    Tagged
    0 Thread(s)
    Sorry to say, your entire home installation was done incorrectly. Fortunately, you found the A/Cs were not damaged!!!
    Rob & Nikki + Cloverfield
    2020 Grand Design Solitude S-Class 3350RL
    2015 RAM 3500 Longhorn Laramie Crew Cab, Long Bed, 4x4 Dually Cummins/AISIN

    Mountains of Pennsylvania

  5. #5
    Site Team Member traveldawg's Avatar
    Join Date
    Aug 2017
    Location
    Florida Space Coast
    Posts
    4,038
    Blog Entries
    1
    Mentioned
    100 Post(s)
    Tagged
    0 Thread(s)
    You probably want an electrician (one that is licensed and has a good reputation backed up by a reputable company) come and check your wiring (house and extension outlets).

    As most others said, ACs like good voltage. I've found that mine don't much care for anything under 110 or maybe 109.

    My PEI EMS cuts off electric at 104.
    Larry KE4DMG
    2022 F-350 KRU SRW LB - Airlift 5000+, ForScan, 37 RDS Aux Tank,
    2019 310GK-R - Sailuns; MorRyde IS; Disc Brakes; 20K Reese Goosebox
    Search kalakamods for my mods


  6. #6
    Rolling Along
    Join Date
    Mar 2021
    Posts
    585
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    For a 30A run between 150 and 200 feet, you would need to use 4ga. cable.
    You really need a licensed electrician to do the pedestal wiring. He also needs to be aware that this is 120V AC and not 240V.The Internet abounds with stories of pedestal 30A outlets being wired with 230V, two hots across the terminals instead of a neutral and a hot. That works great for dryers, RVs, not so well.
    2010 Jayco 26(SOLD)
    2011 Keystone Outback 277RL(SOLD)
    2021 Grand Design 268BH
    2013 Ford F250 XLT, 6.2L Gas

  7. #7
    Big Traveler gbkims's Avatar
    Join Date
    Mar 2017
    Location
    Pearland, TX
    Posts
    1,709
    Mentioned
    15 Post(s)
    Tagged
    0 Thread(s)
    I compared a run at my home to the estimated voltage drop by the Southwire online calculator.
    CB Panel to Storage Bldg subpanel, ~90' run of 10 Awg in buried conduit.

    https://www.southwire.com/calculator-vdrop
    "1 conductor per phase utilizing a 10 AWG Copper conductor installed Direct Buried will limit the voltage drop to 3.15% or less when supplying 20 amps for 90.0 feet on a 120 volt 1 phase system."

    120V Outlet, no load.
    Click image for larger version. 

Name:	Storage Bldg wo Load 122.7 VAC - 2021-07-03.jpg 
Views:	6 
Size:	94.9 KB 
ID:	35232

    Suretest 61-165 Tests:
    Click image for larger version. 

Name:	Storage Bldg 120V Outlet Vd 3.4% 118.5 VAC - 12A Test w Ideal 61-165 - 2021-07-03.jpg 
Views:	6 
Size:	89.4 KB 
ID:	35233

    Click image for larger version. 

Name:	Storage Bldg 120V Outlet Vd 4.2% 117.4 VAC - 15A Test w Ideal 61-165 - 2021-07-03.jpg 
Views:	6 
Size:	75.8 KB 
ID:	35234

    Click image for larger version. 

Name:	Storage Bldg 120V Outlet Vd 5.6% 115.7 VAC - 20A Ideal 61-165 Test - 2021-07-03.jpg 
Views:	6 
Size:	90.2 KB 
ID:	35235
    - Gene

    Kim & Gene
    2015 Reflection 317RST
    2017 Ram 3500 CC LB 4x2 6.7 CTD AISIN 3.73 DRW Auto Level Rear Air, BD3, Prodigy P3, Aux Tank

  8. #8
    Site Sponsor SolarPoweredRV's Avatar
    Join Date
    Mar 2019
    Location
    Tampa Florida
    Posts
    2,146
    Mentioned
    113 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by xrated View Post
    117-118 VAC at the panel is considered a bit low. Most newer residences will see voltages in the 123-125VAC range, and of course on high electrical demand (think summer A/C units running by everyone that is on that transformer feed, can suck the voltage down considerably. On top of the "lower voltage" numbers at the house pedestal, you are using a 175' of some type of wiring to the RV. There will be additional voltage drop associated with that length of the circuit. It's likely that if you test the voltage at the end of the 175' run and do not have it connected to anything, thus NOT pulling a load on it, it will read very similar to the voltage at the house pedestal. Voltage drop occurs when a load is placed on the wires that feed the load. If you were to hook up the trailer and turn an A/C unit on you would likely see that the voltage at the breaker panel in the trailer is now maybe 8-10 volts less.

    In my opinion, you have two different issues that are affecting you. 1. The no load voltage at the house panel. 2. The length of the run feeding the trailer is likely not sized correctly for that distance and is causing some voltage drop. You said that you didn't know what size those wires were, so that is still an unknown at this point in time. Other possibilities include loose connections anywhere along the path to your RV....including at the house breaker panel, any terminations from there to the receptacle that you are plugging the trailer into, as well as possibly in the trailer itself.....although you did say that it performed OK when at the dealership's 50A shore power plug.

    The revers polarity indication needs to be corrected.....and if you have no real working knowledge or skills with electrical equipment, I would suggest hiring an Electrician that does. It is possible for the wiring to be reversed at the home breaker panel or at the 30A outlet that you plug into or any other terminations that might be in between those locations....if there are any. The bottom line though, it needs to be corrected. I don't believe that issue is causing the lower voltage issues you are experiencing, and I did state my thoughts about the why of the lower than normal voltage readings.....so basically, I would focus on finding out and fixing the reverse wiring issue, then the size of the 175' of wire feeding the trailer plug, and if necessary, you may have to replace that 175' run with a larger ga. wiring.
    I agree with the above.

    Additionally, I think your Electrician installed too small Gauge wire for your 175 foot run.

    You also might have an Electrician look at your house wiring because you are starting a few volts low, and then you are running 175 feet to the camper.

    I might also guess that your Electrician calculated the voltage loss on the wire based on 240 volts and not 120 volts for the pedestal.

    You also want to know weather the Electrician used Copper wire or Aluminum wire, either is OK, you just need to up-size the Aluminum wire.

    Here is one final tip that will fix your issue...

    Install a Hughes AutoFormer at the pedestal. The Hughes AutoFormer will increase the voltage going into your camper and your A/Cs will run right. I have one and it works well (I don't need it on my new coach because I have a Hybrid Inverter).
    David and Peggy
    2019 Ford F350 Lariat, 6.7L Diesel, Dually, Long Bed
    Running with 20k Reese Goosebox (Love It) and Ford Factory "Puck" system.
    Stopping with 8,000 lb Disc Brakes and Titan Hydraulic over Electric Brakes system.
    Powering all this fun with 1200 Watts of Solar, two Tesla, Model S, battery modules, 24 volt Victron Inverter.
    2018 Solitude 310 GK

  9. #9
    Site Sponsor
    Join Date
    Aug 2013
    Posts
    2,153
    Mentioned
    7 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by BobLandry View Post
    For a 30A run between 150 and 200 feet, you would need to use 4ga. cable.
    You really need a licensed electrician to do the pedestal wiring. He also needs to be aware that this is 120V AC and not 240V.The Internet abounds with stories of pedestal 30A outlets being wired with 230V, two hots across the terminals instead of a neutral and a hot. That works great for dryers, RVs, not so well.
    This is the most important comment on this thread. Do not let an electrician hook your 30 Amp plug up as a 230 dryer plug. RV's run on 120 volts only.

    I ran a 200 line to a pedestal (50/30/20) typical RV box and used 2ga wire. I have strong voltage at the box.

    Red
    Location - Wherever the road takes us...Full-timers
    2015 Momentum 380
    2019 Ram Dually

  10. #10
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,704
    Mentioned
    144 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by el Rojo View Post
    This is the most important comment on this thread. Do not let an electrician hook your 30 Amp plug up as a 230 dryer plug. RV's run on 120 volts only.

    I ran a 200 line to a pedestal (50/30/20) typical RV box and used 2ga wire. I have strong voltage at the box.

    Red
    Have you checked the actual voltage while that circuit is under a substantial load......A/Cs on, water heater on, other electrical devices running? The voltage will not drop when there is no load on the circuit.

    And quite honestly, any "Electrician" that hooks up a 30A RV receptacle for 240VAC....IS NOT AN ELECTRICIAN....Period! There are lots of folks out there working as "Electricians".....who really don't have a clue about what they are doing. I spent 4 years going through an apprenticeship, as did lots and lots of Journeymen Electricians and it is downright scary what some of the "hacks" are doing in the name of being an Electrician.
    Last edited by xrated; 07-04-2021 at 07:12 AM.
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.