    Question for an electrician?

    Years ago, we bought a portable generator for the house after being without power for over a Christmas week with zero temps, heavy snow, heat by fireplaces. Had an electrician install the correct sub-panel dedicated to the genset and an outlet on the exterior of the garage wall (4 pin male 30amp/250V connection for the generator) to support our well pump which runs at 220V.

    Now the question. Trying to have a tech install Coleman soft-starts on the 310 but other than a 110V 15amp garage outlet, the nearest is the connection to the generator. I'm assuming that electricity can flow both ways here since my procedure is to shut the main power supply to the street off before engaging the generator. I want to be able to test the install (mobile tech). Can I leave the master switch for the generator sub-panel and street ON and provide 30 amps to the coach? I could run the on-board generator, but that doesn't really tell me if the soft-starts will work on less than 50amps.
    TIA
    Last edited by ajg617; 05-28-2023 at 07:00 PM.
    Robin & John
    2020 Ram 3500 LB SRW 4WD Crew Laramie 6.7HO Aisin, 55gal Titan
    2022 Solitude 310GK-R - Dual pane, factory solar & Onan, 8K axles with discs, 18K GVWR, W/D, Heat Pump, Goosebox, Battleborn

    2023 stays

  2. #2
    Long Hauler huntindog's Avatar
    Join Date
    Nov 2017
    Posts
    2,175
    Mentioned
    33 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ajg617 View Post
    Years ago, we bought a portable generator for the house after being without power for over a Christmas week with zero temps, heavy snow, heat by fireplaces. Had an electrician install the correct sub-panel dedicated to the genset and an outlet on the exterior of the garage wall (4 pin male 30amp/250V connection for the generator) to support our well pump which runs at 220V.

    Now the question. Trying to have a tech install Coleman soft-starts on the 310 but other than a 110V 15amp garage outlet, the nearest is the connection to the generator. I'm assuming that electricity can flow both ways here since my procedure is to shut the main power supply to the street off before engaging the generator. I want to be able to test the install (mobile tech). Can I leave the master switch for the generator sub-panel and street ON and provide 30 amps to the coach? I could run the on-board generator, but that doesn't really tell me if the soft-starts will work on less than 50amps.
    TIA
    I am not an Electrician but, I am pretty sure that what this past electrician did is not to code. The correct install should not require you to remember to do anything.
    2021 398M Full Body Paint 8k axles. LRH tires. Disc brakes.
    Two bathrooms, no waiting 155 fresh, 104 black, 104 grey 1860 watts solar.
    800AH BattleBorn Batteries No campgrounds 100% boondocking
    2020 Silverado High Country 3500 dually crewcab Duramax Allison

  3. #3
    Site Sponsor ajg617's Avatar
    Join Date
    Jul 2020
    Location
    New Hampshire
    Posts
    2,381
    Mentioned
    30 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by huntindog View Post
    I am not an Electrician but, I am pretty sure that what this past electrician did is not to code. The correct install should not require you to remember to do anything.
    Should have probably said this was probably 15 years ago and I should have clarified it's a portable generator on wheels that I roll out and connect with a cable much like what is in our coach. Permit was pulled and inspector came out. So it was to code then - no electronic switching involved at all - all manual.
    Robin & John
    2020 Ram 3500 LB SRW 4WD Crew Laramie 6.7HO Aisin, 55gal Titan
    2022 Solitude 310GK-R - Dual pane, factory solar & Onan, 8K axles with discs, 18K GVWR, W/D, Heat Pump, Goosebox, Battleborn

    2023 stays

  4. #4
    Site Sponsor Jerryr's Avatar
    Join Date
    Nov 2016
    Location
    Florida
    Posts
    2,822
    Mentioned
    30 Post(s)
    Tagged
    0 Thread(s)
    Your electrician likely installed a manual portable generator power transfer kit, not a sub panel. Totally legal.

    It has an additional box that can power certain circuits off a generator rather than the grid if needed

    I’ve got one that I need to install at my cabin so I can run the well 240 v pumps, fridge, fans and some lights during power outages. I’ve got this one https://www.amazon.com/Reliance-Corp...000HS2L3O?th=1
    Jerry & Linda
    Emma & Abby our Mini Golden Doodles & JR our Amazon Parrot
    2017 Reflection 337RLS, Build Date 01/2017, Titan Disk Brakes, Goodyear G614s 235/85/16 G Rated tires
    2022 F-450 King Ranch Ultimate, 4,868 lb Payload, Bedrug Bedliner, Andersen Ultimate II Aluminum 5th wheel hitch
    http://visitedstatesmap.com/image/FLGANCSCsm.jpg

  5. #5
    Seasoned Camper
    Join Date
    Jul 2017
    Location
    Near Birmingham, AL
    Posts
    372
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Short answer: No.

    That is a transfer switch, not a subpanel.


    When you throw the switch to the mains, it disconnects the generator connection.
    2023 Reflection 315RLTS
    2017 Ford F-350 Crew Cab Short Bed SRW, 6.7L Diesel
    Hensley Swift Arrow

  6. #6
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,355
    Mentioned
    135 Post(s)
    Tagged
    0 Thread(s)
    There are two ways to connect a generator to a house panel, both code approved if done correctly. 1. via the use of an automatic or a manual transfer switch. 2. Using a breaker lockout device that is attached to the main panel. With that device, you have to turn the main panel breaker off, then slide a lockout bar up and out of the way and then you can turn on the generator input breaker. So it's either the main breaker on, and the generator input breaker off.....or vice versa. With that setup, you also need to have a generator that does not have the neutral/ground bonding on the generator itself.
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

  7. #7
    Long Hauler huntindog's Avatar
    Join Date
    Nov 2017
    Posts
    2,175
    Mentioned
    33 Post(s)
    Tagged
    0 Thread(s)
    Like I said. I am not an Electrician.... But I knew it had to be setup so that it was fail safe. IOW impossible to screw it up by forgetting to flip the main breaker off.
    2021 398M Full Body Paint 8k axles. LRH tires. Disc brakes.
    Two bathrooms, no waiting 155 fresh, 104 black, 104 grey 1860 watts solar.
    800AH BattleBorn Batteries No campgrounds 100% boondocking
    2020 Silverado High Country 3500 dually crewcab Duramax Allison

  8. #8
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,355
    Mentioned
    135 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by huntindog View Post
    Like I said. I am not an Electrician.... But I knew it had to be setup so that it was fail safe. IOW impossible to screw it up by forgetting to flip the main breaker off.
    I use the breaker lockout method on my backup generator setup on the house. I've got a 12,000W running (15,000W peak), dual fuel Westinghouse with a built in CO sensor on it to power some of the house in case of a utility outage. It of course feeds the house breaker panel via a double pole 50A breaker on the right side of the panel, the top breaker....which is locked out until I turn off the 200A house main. Everything is manually operated by me, and I've typed out a set of very specific instructions that list the order/sequence of how to get the generator online, as well as how to restore utility power. It's not so much for me, but in case my wife would need to use it (not likely I guess, but still possible). I also have a Reliance "PowerBack" on the system to notify me when the utility power has been restored....with a 100+ db screeching sound. In addition to the PowerBack, I also wired in a wireless module that is specific to my Honeywell brand Security system that is on the house....and the module sends a signal to my alarm panel (which is operating whether I'm on utility power or generator power) and it lets me know that utility power has been restored with a pop up on the screen and a beep about every 20 seconds or so. Using the breaker lockout was the least expensive option and realistically, I don't need fully automatic and very expensive automatic transfer stuff to switch over and get me back on line. That, plus my genny is NOT a whole house standby type generator that is on a pad outside the house, it is a portable (if 350 lbs of generator is really portable??? ) that has to be wheeled out of the garage and setup.

    Our house has an Electric Heat pump for heating/cooling, so the power draw isn't terrible....unless, it's cold enough that the heat pump cannot keep up, then a 10Kw electric heat strip kicks on (aux. heat option) and that of course takes a high percentage of the generator power to operate. If that situation arises in the winter time, you definitely have to manage what you have running in the house and turn off anything/everything that is not totally necessary. We do have a gas fireplace that is propane, so I can run that also to help supplement the heat pump usage...if needed, but we rarely get those kind of temperatures in E. TN.
    Last edited by xrated; 05-29-2023 at 05:55 AM. Reason: added info.
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

  9. #9
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,355
    Mentioned
    135 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ajg617 View Post
    Years ago, we bought a portable generator for the house after being without power for over a Christmas week with zero temps, heavy snow, heat by fireplaces. Had an electrician install the correct sub-panel dedicated to the genset and an outlet on the exterior of the garage wall (4 pin male 30amp/250V connection for the generator) to support our well pump which runs at 220V.

    Now the question. Trying to have a tech install Coleman soft-starts on the 310 but other than a 110V 15amp garage outlet, the nearest is the connection to the generator. I'm assuming that electricity can flow both ways here since my procedure is to shut the main power supply to the street off before engaging the generator. I want to be able to test the install (mobile tech). Can I leave the master switch for the generator sub-panel and street ON and provide 30 amps to the coach? I could run the on-board generator, but that doesn't really tell me if the soft-starts will work on less than 50amps.
    TIA
    The soft start doesn't care whether you are on a 30A setup or a 50A setup. It's made to be installed on a 120VAC circuit, provided that your A/C unit is 120VAC, and every RV A/C unit that I've ever seen is just that....120VAC
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

  10. #10
    Site Sponsor
    Join Date
    May 2018
    Location
    Central FL
    Posts
    690
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    What power source are you going to use which makes you need the soft starts? Using that to test them after install would be my first choice. It also seems to me the test for the soft starts could be to use the 15 amp 120vAc garage outlet with the proper dogbone adapter.
    2022 Reflection150 226RK
    2022 F150 Powerboost hybrid with 3.5L Ecoboost


Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.