    Quote Originally Posted by toolman.dustin View Post
    Can you plug your RV into a 220 volt welding outlet or a 220 volt dryer outlet: YES, I do it all the time at my house.
    But, the fact you're asking the question means you don't know you can and don't know how; so you probably shouldn't try.

    Read these 12-13 articles as many times as it takes to understand it: https://www.myrv.us/electric/
    If you can't understand it then don't try and build a welding receptacle "dogbone" connector.

    At the RV park receptacle: you're 50 amp receptacle is actually two 50 amp, 110 volt circuits in a single receptacle.
    Do your really need 100 amps? Very rarely.

    When you connect your 50 trailer to a 30 amp receptacle at the RV park you use an adapter and your are actually connecting your entire trailer to a single 120 volt 30 amp breaker. This is done because inside the adapter there's a jumper that applies power to both of your RV 120 volt lines. This allows you can run all your appliances, but you have to manage which ones, example; you can't run both A/Cs at the same time on 30 amps.

    My garage welder outlet consists of two 30 amp breakers each feeding a 120 volt line providing a total of 220 volts for a total of 60 amps maximum. When I connect my 50 amp trailer "dogbone" to my 220 volt welding outlet in my garage, I'm actually only connecting to one of the 120 volt lines of the 220 volt outlet. I can run anything in the trailer, but I am limited to the 30 amp breaker on that 120 volt line I'm using. Therefore; if my trailer draws more than 30 amps it will trip the breaker in the garage. Therefore, I can not run both air conditioners in the trailer at the same time; I can't run the air conditioner and the microwave at the same time. I have to manage my power consumption. Even if YOU can manage the power consumption, can your spouse or kids when you're not there. I've explained this to my wife over and over, but when we're connect to the garage and she's packing the trailer she always try's to run both A/Cs and on occasion the microwave and tripping the breakers is pretty common. Then she calls me says the power went off, I need to come home and fix it. Just food for thought.

    Can you run you're RV from a welding outlet: yes, but you will not find anywhere a dogbone adapter of any kind sold for adapting your welding receptacle or clothes dryer to your RV because not enough people understand what they're doing.

    If you don't know what you're doing it's very risky, you could burn your trailer down or worse electrocute someone; not to mention burn up your air conditioner or microwave of some other appliance. A better choice might be to buy a 4500 watt generator, it may be noisier, but it's safer.

    just FYI,
    Dustin
    What welder outlet do you have that has 4 pins?
    John & Kathy
    2014 F250 Lariat FX4 6.2L SBCC
    2014 Reflection 303RLS
    SW Indiana

  2. #32
    Site Team Redapple63's Avatar
    Join Date
    Mar 2020
    Location
    SoCal
    Posts
    2,761
    Mentioned
    26 Post(s)
    Tagged
    0 Thread(s)
    @Traveldwg had the best method for you.

    First make sure it is the correct receptacle.

    Second, using a multi-meter check between leg 1 and ground for 110v
    leg 2 and ground for 110v
    leg 1 and common/neutral for 110v
    leg 2 and common/neutral for 110v
    leg 1 and leg 2 for 220v

    As several have pointed out DO NOT CONNECT TO A 3 PRONG WELDING RECEPTACLE it will cause damage.

    Good Luck,
    Bill
    2019 GMC 3500 SRW Sierra Denali Duramax
    2020 Reflection 315RLTS

  3. #33
    Seasoned Camper
    Join Date
    Apr 2019
    Location
    Kansas
    Posts
    131
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jkwilson View Post
    What welder outlet do you have that has 4 pins?
    It isn't, it's a 3 pin, 250v outlet: NEMA 6-50R, 2-pole, 3-wire, grounding, rated 50A 240V No Neutral
    My garage welder outlet consists of two 30 amp breakers each feeding a 120 volt line providing a total of 220 volts for a total of 60 amps maximum. When I connect my 50 amp trailer "dogbone" to my 220 volt welding outlet in my garage, I'm actually only connecting to one of the 120 volt lines of the 220 volt outlet. I can run anything in the trailer, but I am limited to the 30 amp breaker on that 120 volt line I'm using. Therefore; if my trailer draws more than 30 amps it will trip the breaker in the garage. Therefore, I can not run both air conditioners in the trailer at the same time; I can't run the air conditioner and the microwave at the same time. I have to manage my power consumption.

    Dustin
    Dustin and Doris

    2018 2600RB
    2016 Tundra: 5.7L with towing package.

  4. #34
    Site Sponsor
    Join Date
    Jul 2017
    Location
    SW Indiana
    Posts
    1,956
    Mentioned
    42 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by toolman.dustin View Post
    It isn't, it's a 3 pin, 250v outlet: NEMA 6-50R, 2-pole, 3-wire, grounding, rated 50A 240V No Neutral
    My garage welder outlet consists of two 30 amp breakers each feeding a 120 volt line providing a total of 220 volts for a total of 60 amps maximum. When I connect my 50 amp trailer "dogbone" to my 220 volt welding outlet in my garage, I'm actually only connecting to one of the 120 volt lines of the 220 volt outlet. I can run anything in the trailer, but I am limited to the 30 amp breaker on that 120 volt line I'm using. Therefore; if my trailer draws more than 30 amps it will trip the breaker in the garage. Therefore, I can not run both air conditioners in the trailer at the same time; I can't run the air conditioner and the microwave at the same time. I have to manage my power consumption.

    Dustin
    What you are doing is unsafe, and may be a huge fire risk depending on the wiring.

    You are drawing current through the EGC, which is a huge code and safety violation. You may also be significantly overloading the EGC since is is often smaller than the current carrying conductors on a circuit. The EGC MAY not be large enough to handle 30A.

    There is no good way to operate a 120V device on a 240V circuit that doesn’t have a neutral.
    John & Kathy
    2014 F250 Lariat FX4 6.2L SBCC
    2014 Reflection 303RLS
    SW Indiana

  5. #35
    Seasoned Camper
    Join Date
    Apr 2019
    Location
    Kansas
    Posts
    131
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jkwilson View Post
    What you are doing is unsafe, and may be a huge fire risk depending on the wiring.

    You are drawing current through the EGC, which is a huge code and safety violation. You may also be significantly overloading the EGC since is is often smaller than the current carrying conductors on a circuit. The EGC MAY not be large enough to handle 30A.

    There is no good way to operate a 120V device on a 240V circuit that doesn’t have a neutral.
    You're correct, there's no good, code approved way to do this. In my situation, the electrician who wired my garage/house (before I moved in) pulled 4 strand, 10 gauge wire. He connect both the neutral (white) and ground (bare) to the welding receptacle ground pin AND connected both the neutral (white) and ground (bare) to the neutral buss (white) in the breaker panel. So basically, because they are in parallel, they become a 6 gauge wire. And the welding outlet is basically "self bonded". Regardless, the ground and neutral buss bars in the breaker panel (in the house) are bonded anyway so it works for me because I understand and the EGC is not overloaded. But, it's not to code when I connect my trailer for loading and unloading and if an electrical short to chassis in appliance occurred in my trailer I'm counting on at least one of the many circuit breakers in the path to trip. We all make that assumption all the time with electrical appliances. I could also bond it in the RV electrical panel, but then I'd have to bond when I'm at home and unbond when I'm traveling and it's not worth the exercise.

    There were suggestions to the OP to replace the welding receptacle (NEMA 6-50R) with an RV 50 amp receptacle, (NEMA 14-50R) but that would only work properly if there was 4 strand wire already pulled when the house/garage was wired. In my case, I could actually add a NEMA 14-50R outlet next to my welding outlet, and jumper it over to my welding receptacle, I guess. I use my welder fairly often so I'm not going to replace the outlet but I'll consider adding the RV receptacle...... actually no; if I did that then I'd have to purchase another 50 feet of RV, 50 amp power cord to extend all the way to the welding receptacle at the back of my garage. So, I don't need to fix what's already working.

    This is a very hot topic and a serious safety issue if not really understood. And there are going to be more "opinions" about how/can/should I do this than "what's the best": air compressor, generator, or weight distribution hitch.
    So, my advise is, if you don't understand what's going on then learn before you try.

    On two occasions I've gone to friends houses that had wiring done by "electricians" that were wired incorrectly. On three occasions I've stayed in RV parks that have wiring problems in the pedestal (which is why I use the Hughes Bulldog RV Power Watchdog). It's too important to take for granted. The solution is to "seek to understand" don't just ask for opinions.

    Dustin
    Last edited by toolman.dustin; 03-13-2022 at 12:28 PM. Reason: spelling correction
    Dustin and Doris

    2018 2600RB
    2016 Tundra: 5.7L with towing package.

  6. #36
    Site Team xrated's Avatar
    Join Date
    Feb 2019
    Location
    "Murvul", TN
    Posts
    3,357
    Mentioned
    135 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by toolman.dustin View Post
    You're correct, there's no good, code approved way to do this. In my situation, the electrician who wired my garage/house (before I moved in) pulled 4 strand, 10 gauge wire. He connect both the neutral (white) and ground (bare) to the welding receptacle ground pin AND connected both the neutral (white) and ground (bare) to the neutral buss (white) in the breaker panel. So basically, because they are in parallel, they become a 6 gauge wire. And the welding outlet is basically "self bonded". Regardless, the ground and neutral buss bars in the breaker panel (in the house) are bonded anyway so it works for me because I understand and the EGC is not overloaded. But, it's not to code when I connect my trailer for loading and unloading and if an electrical short to chassis in appliance occurred in my trailer I'm counting on at least one of the many circuit breakers in the path to trip. We all make that assumption all the time with electrical appliances. I could also bond it in the RV electrical panel, but then I'd have to bond when I'm at home and unbond when I'm traveling and it's not worth the exercise.

    There were suggestions to the OP to replace the welding receptacle (NEMA 6-50R) with an RV 50 amp receptacle, (NEMA 14-50R) but that would only work properly if there was 4 strand wire already pulled when the house/garage was wired. In my case, I could actually add a NEMA 14-50R outlet next to my welding outlet, and jumper it over to my welding receptacle, I guess. I use my welder fairly often so I'm not going to replace the outlet but I'll consider adding the RV receptacle...... actually no; if I did that then I'd have to purchase another 50 feet of RV, 50 amp power cord to extend all the way to the welding receptacle at the back of my garage. So, I don't need to fix what's already working.

    This is a very hot topic and a serious safety issue if not really understood. And there are going to be more "opinions" about how/can/should I do this than "what's the best": air compressor, generator, or weight distribution hitch.
    So, my advise is, if you don't understand what's going on then learn before you try.

    On two occasions I've gone to friends houses that had wiring done by "electricians" that were wired incorrectly. On three occasions I've stayed in RV parks that have wiring problems in the pedestal (which is why I use the Hughes Bulldog RV Power Watchdog). It's too important to take for granted. The solution is to "seek to understand" don't just ask for opinions.

    Dustin
    Unfortunately there are LOTS of folks working as "Electricians", that barely know the difference between conduit and a condominium....other than they both start with the letter "C".
    2016 F350 CrewCab Dually
    2018 Momentum 394M...Heavily Modded!
    2023 Suzuki GSX-S1000 GT+
    Excessive Payload is a Wonderful Thing

    "If it ain't fast....It ain't Fun"

  7. #37
    Fireside Member jungleb0y's Avatar
    Join Date
    Jan 2019
    Location
    Palm Coast, FL
    Posts
    55
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)

    Smile

    Quote Originally Posted by firedreamer2 View Post
    Going to spend a week at a friend's house and he says he has power for me. He added a 220 line to run a welder and says i can use the for our 5th wheel (50 amp rig) He doesn't recall the type of plug off hand but will send me a pic. I'm wondering if that would be the same power as the 50 amp pedestals in RV parks and safe to use. I seam to recall its "Not"
    Thanks
    Sure you can do that, but you have to understand how to wire the adapter to make it happen.
    With the welder outlet you will have to verify it's a 250v outlet 3 prong common for dryers (use a meter to verify this), this will have the 2 hot lines (red and black) connected to the blades and the ground (green) connected to the gumdrop looking one.

    The adapter you need to have made takes the red and black lines and connects them to the outsides blades of the 50A RV and then the green line get's bridged between the gumdrop blade and the straight blade directly across from it (mean for the white). It's not the ideal solutions but it works , the ground isn't usually the same gauge as the neutral and could have the potential to cause fire issues over longer runs and high amp draws, and when you mention it you stir up everything and get tensions running kinda like talking politics or something.

    Anyway yeah you can do it, you'll just need to have an adapter made as mentioned before you can't buy that but the big box hardware will have what you need.


    Quote Originally Posted by firedreamer2 View Post
    safe to use. I seam to recall its "Not"
    We all have risks that we accept driving down the road pulling a camper is one of them but we overcome.
    Attached Thumbnails Attached Thumbnails thisnthat.jpg  
    The only thing that works on a RV is the owner...
    Jared - 315RLTS - 2500HD

  8. #38
    Site Sponsor
    Join Date
    Nov 2019
    Location
    S. E. PENNSYLVANIA
    Posts
    919
    Mentioned
    15 Post(s)
    Tagged
    0 Thread(s)
    PLEASE DON'T DO what toolman.dustin or jungleb0y have done... you could end up getting someone killed!

    This diagram is so unsafe it's not even funny.

    Click image for larger version. 

Name:	Screenshot_20220313-233412_Chrome.jpg 
Views:	75 
Size:	18.6 KB 
ID:	39402

    I'm a retired electrician with 40+ years in all aspects of the trade and trust me when I tell you that neither of these are good remedies for your situation! If there is no 4 wire 50A cable at the welding receptacle there is no SAFE way to do it.... especially for non trained personel. You would be better off to switch everything you can over to gas and just run your RV on a 20A 120V dedicated line and only use the bare minimum in your RV.
    If you look at the jacket on the cable feeding the welder outlet it will tell you what wires are in it. If by chance there are 4 wires there with 3 of them being insulated #6AWG and the 4th being a bare or green ground then it can safely be changed out to a 50A RV receptacle by a qualified person. The opposite end in the residential electrical panel would also need to be checked to verify everything is terminated correctly.
    Bill & Colleen ~ Schwenksville, Pa
    2019 Reflection 337RLS
    2006 GMC Sierra 3500 8.1L V-8
    Firestone Ride-Rite Air Bags
    Front Stabilizer Bar
    Rear Anti Sway Bar

  9. #39
    Fireside Member jungleb0y's Avatar
    Join Date
    Jan 2019
    Location
    Palm Coast, FL
    Posts
    55
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by IBEW Sparky View Post
    PLEASE DON'T DO what toolman.dustin or jungleb0y have done... you could end up getting someone killed!

    This diagram is so unsafe it's not even funny.

    Click image for larger version. 

Name:	Screenshot_20220313-233412_Chrome.jpg 
Views:	75 
Size:	18.6 KB 
ID:	39402
    Here's one of them things on amazon that will get ya killed, better use with caution!!
    Click image for larger version. 

Name:	41UK9Z7+OcL._AC_SR320,320_.jpg 
Views:	12 
Size:	11.2 KB 
ID:	39406
    https://www.amazon.com/dp/B09P1BP4ZQ...NsaWNrPXRydWU=
    The only thing that works on a RV is the owner...
    Jared - 315RLTS - 2500HD

  10. #40
    Site Sponsor
    Join Date
    Nov 2019
    Location
    S. E. PENNSYLVANIA
    Posts
    919
    Mentioned
    15 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jungleb0y View Post
    Here's one of them things on amazon that will get ya killed, better use with caution!!
    Click image for larger version. 

Name:	41UK9Z7+OcL._AC_SR320,320_.jpg 
Views:	12 
Size:	11.2 KB 
ID:	39406
    https://www.amazon.com/dp/B09P1BP4ZQ...NsaWNrPXRydWU=

    And I still wouldn't use it for an RV with a 50A. power cord setup. The ground on a straight 250V dryer receptacle is not sized to handle the load requirements of an RV with 50A power.
    Can you please show me the UL listing on it?
    How about the CSA listings on it?

    In case anyone doesn't understand UL listings....

    Click image for larger version. 

Name:	Screenshot_20220314-052751_Chrome.jpg 
Views:	10 
Size:	102.3 KB 
ID:	39407
    Bill & Colleen ~ Schwenksville, Pa
    2019 Reflection 337RLS
    2006 GMC Sierra 3500 8.1L V-8
    Firestone Ride-Rite Air Bags
    Front Stabilizer Bar
    Rear Anti Sway Bar

Page 4 of 7 FirstFirst ... 23456 ... LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.