I'm looking at installing a 50A outlet at home and would like confirmation/feedback as to whether or not the following links are the right direction I need to follow.
http://www.myrv.us/electric/Pg/50amp_Service.htm
http://www.myrv.us/Imgs/PDF/50-amp%20Service.pdf
http://www.myrv.us/electric/index.htm
-
04-27-2019, 09:40 AM #2
- Join Date
- Sep 2018
- Location
- Ontario, Canada
- Posts
- 1,438
- Mentioned
- 18 Post(s)
- Tagged
- 0 Thread(s)
If you are not sure about what you are doing I would have an electrician wire it for you. May be a lot cheaper than missing something and damaging the trailer, house or a fire. JMHO.
RobRob & Barb
2022 Solitude 378MBS
2022 RAM 3500 SRW HO Aisin 4x4
Waterloo, Ontario, Canada
-
04-27-2019, 10:44 AM #3
- Join Date
- Oct 2016
- Posts
- 1,539
- Mentioned
- 13 Post(s)
- Tagged
- 0 Thread(s)
If you are using NM-B cable to wire this circuit you need to use #6/3 with ground. A couple of your links refer to using #8 if under 25ft. This is only good for 40 amps in NM-B configuration.
-
04-27-2019, 07:57 PM #4
- Join Date
- Nov 2016
- Location
- Southern Indiana
- Posts
- 751
- Mentioned
- 7 Post(s)
- Tagged
- 0 Thread(s)
NEMA 14-50R is the correct receptacle to purchase. #6-3 copper wire with a 50 Amp double pole breaker. The wiring diagrams shown in the attachments you posted are correct. As someone else suggested before if you are uncertain about what you are doing you should hire an electrician to complete the work. This may be a good opportunity to invest in a power management/surge protector. I never plug our fifth wheel in without one. I have the 50 amp SurgeGuard portable unit by Southwire. When I first installed our home 50amp receptacle I knew that if I had something screwed up the SurgeGuard unit would catch it and prevent a power issue causing problems with the RV electrical system. Good luck!
The Adams - 2017 Reflection 367BHS, 2019 F-350 6.7L PSD 4x4 CC DRW, B&W hitch on Ford pucks, Air Lift Loadlifter 5000 Ultimate Plus air bags, "Rupert" the Weimaraner.
-
08-02-2019, 09:33 AM #5
- Join Date
- Oct 2017
- Location
- Central GA
- Posts
- 121
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
I'm trying to have a 50A at the house also. I have read about the errors even electricians make by treating the 50A RV receptacle like a 240V dryer receptacle. I just got off the phone with an electrician that told me that the 50A is 240V and is separated at the breaker box IN the trailer to two 120V legs. He is incorrect, no? I told him I'd let him know.....
I have found this "somewhere" on the internet...
• Do not confuse the 14-50R with the 240-volt household outlet familiar from its use in powering clothes dryers and cookers. They are “common” outlets, meaning the two 120-volt supplies work together to deliver 240 volts to a 240-volt appliance. The 14-50R is an “uncommon” outlet, meaning it delivers two 120 volts currents. Your RV must be thought of as one very large 120-volt appliance. Even certified electricians who are unfamiliar with RVs can mistakenly assume an enormous RV is a 240-volt appliance, but plugging it into a 240-volt supply will destroy all appliances and accessories, and can cause fire. A wrongly-wired 50-amp service can introduce 240 volt electricity to your RV with the same results.RobM
2017 Chevy Silverado 3500 L5P, Transfer Flow 35 Gal Aux Fuel Tank, Pace Edwards Full Metal JackRabbit Tonneau Cover
2018 Solitude 310-GKR, Curt Q-20 puck system hitch, TST TPMS 507, Titan discs
-
08-02-2019, 10:00 AM #6
- Join Date
- Nov 2016
- Location
- Florida
- Posts
- 2,822
- Mentioned
- 30 Post(s)
- Tagged
- 0 Thread(s)
Your electrician is correct. There is nothing in the RV that uses 240 volts. The 240 volts are separated in the RV breaker box to feed 2-120 volt legs.
Your home breaker box does the same. The home main breaker is a double pole 240 volt breaker that feeds 2-120 volt legs. Appliances at home that require 240 volts utilize a double breaker to feed the 2 out if phase 120v legs to the 240 volt appliance like a range, AC or water heater.
A14-50R receptacle is not unusual. Many oven ranges use that receptacle.
Older dryers were 3 wire receptacles, which didn’t have a neutral. 50 amp RVs REQUIRE a Neutral. Newer homes use a 4-wire dryer receptacle.Last edited by Jerryr; 08-02-2019 at 10:24 AM.
Jerry & Linda
Emma & Abby our Mini Golden Doodles & JR our Amazon Parrot
2017 Reflection 337RLS, Build Date 01/2017, Titan Disk Brakes, Goodyear G614s 235/85/16 G Rated tires
2022 F-450 King Ranch Ultimate, 4,868 lb Payload, Bedrug Bedliner, Andersen Ultimate II Aluminum 5th wheel hitch
http://visitedstatesmap.com/image/FLGANCSCsm.jpg
-
08-02-2019, 10:23 AM #7
- Join Date
- Nov 2016
- Location
- Florida
- Posts
- 2,822
- Mentioned
- 30 Post(s)
- Tagged
- 0 Thread(s)
Correct for NM-B, UF etc Romex. . If you run separate stranded THHN or THWN in a raceway (PVC conduit, EMT or Non Metallic Conduit) you can run 8AWG up to about 100 ft by code. 4 each #8 THWN wires easily fits into 3/4 inch PVC conduit.
https://www.cerrowire.com/products/r...pacity-charts/Last edited by Jerryr; 08-02-2019 at 10:27 AM.
Jerry & Linda
Emma & Abby our Mini Golden Doodles & JR our Amazon Parrot
2017 Reflection 337RLS, Build Date 01/2017, Titan Disk Brakes, Goodyear G614s 235/85/16 G Rated tires
2022 F-450 King Ranch Ultimate, 4,868 lb Payload, Bedrug Bedliner, Andersen Ultimate II Aluminum 5th wheel hitch
http://visitedstatesmap.com/image/FLGANCSCsm.jpg
-
08-02-2019, 02:32 PM #8
- Join Date
- Nov 2017
- Location
- Toronto, Canada
- Posts
- 1,974
- Mentioned
- 54 Post(s)
- Tagged
- 0 Thread(s)
@Chiefblueman / @RVRunners I was surprised to read on the site linked by @SpdSurfn above that a Progressive EMS would not necessarily protect against an open Neutral situation.
The "Open Neutral" article at the index link below reports that someone's appliances were destroyed because the park's pedestal had a weak neutral connection, resulting in 200+ volts appearing on one of the 120V legs in the trailer. In the Q&A the author asserts that the EMS won't respond fast enough to this condition to prevent damage and says that load-testing the pedestal every time we hook up is required.
Do you guys have an opinion on that?Mark - 2018 Solitude 310GK - 2017 F-350 diesel SRW short box - Pullrite Superglide hitch
-
08-02-2019, 06:58 PM #9
- Join Date
- Aug 2016
- Location
- Henderson NV
- Posts
- 895
- Mentioned
- 6 Post(s)
- Tagged
- 0 Thread(s)
Jerry, I don't claim to be an electrician, but i do have a working knowledge. Maybe I'm misunderstanding your response but I interpreted RobM's electrician telling him that the 50 A to the RV is 240 volts (L1, L2, G (no neutral)) and the rv breaker box separates that into 2 120V legs (L1, L2, N, G). "50A is 240V and is separated at the breaker box IN the trailer to two 120V legs". If that's what he is saying, wouldn't that be incorrect? Unless I mis-read, his electrician is wanting to wire the plug at the house like an old dryer...
JohnLast edited by LV Naturist; 08-02-2019 at 07:04 PM.
2018 Silverado LTZ 3500HD CC LB 4X4 DRW Duramax/Allison
2019 Momentum 381M w/Full Body Paint
2016 Can Am Spyder F3 Limited Special Series
2017 Can Am Outlander 1000 XT-P
2016 Wrangler Hard Rock Unlimited
1997 Bayliner Capri 1950 affectionately named Skinnydipper
MSgt, USAF (Ret)
[SIGPIC][/SIGPIC]
-
08-02-2019, 08:30 PM #10
- Join Date
- Nov 2016
- Location
- Florida
- Posts
- 2,822
- Mentioned
- 30 Post(s)
- Tagged
- 0 Thread(s)
If the electrician was considering wiring as an old 3-wire dryer he is incorrect. A 3 wire dryer does not have a neutral which is required to provide 120 volts.
I am not an electrician but in my previous employment we sold equipment that required a 50 amp 14-50R receptacle. We would provide the receptacle to the customer and their electrician would wire it. I’ve checked 100’s of 14-50R receptacles for proper wiring. About 10% of the time professional electricians had wired them incorrectly.
This is the correct wiring of a 14-50R
Last edited by Jerryr; 08-02-2019 at 08:32 PM.
Jerry & Linda
Emma & Abby our Mini Golden Doodles & JR our Amazon Parrot
2017 Reflection 337RLS, Build Date 01/2017, Titan Disk Brakes, Goodyear G614s 235/85/16 G Rated tires
2022 F-450 King Ranch Ultimate, 4,868 lb Payload, Bedrug Bedliner, Andersen Ultimate II Aluminum 5th wheel hitch
http://visitedstatesmap.com/image/FLGANCSCsm.jpg
frame flex problems
Today, 01:45 PM in General Discussion