    Quote Originally Posted by MoonShadow_1911 View Post
    Okay, I noticed that no one addressed your concern about having the generator in the RV, thus it's grounded to the RV.

    First, most generator/inverters are internally grounded. That means all the grounds go to a single point, usually on the frame. They also usually have protections that prevent a "hot chassis".

    Second, the neutral bond does not direct voltage to the chassis ground. For all in intents and purposes, the neutral does not carry voltage for a standard 110 vac line (like in your stix-n-brix house). Now, move to 230 vac, and the "neutral line now carries 110 vac. So, for the generator, all you are doing, with the bonded neutral, is tying the ground and neutral together, "fooling" the EMS into thinking it's connected to a power company 110 vac source.

    Some background: generators leave the neutral "floating", meaning not tied to anything. The EMS sees that it cannot "test" the neutral line because there is no end point. When you tie the neutral with ground, via a bonded neutral plug (as shown in previous posts), you are giving the neutral an end point, thus the EMS things all is good.

    EDIT: the 230 vac example is not really how 230 vac is wired, you have hot, hot, neutral, ground. It was an poor example that hopefully got the image across.

    Sent from my SM-N986U using Tapatalk
    Thanks for the extra detail Mark.
    I missed that the generator is in the rv. I don't think it matters because it's designed to be self contained.

    Rob
    Is the generator mounted on a slide out or what?

    KEN
    Backpacker and tent camper all my life, including BSA as a kid and adult.
    Motorcycle trips across the USA with a tent - 1978 to Present.
    02-10-2005 - 2002 F350 SWD PSD and 2003 Citation 10'8S mostly for Crater Lake Ski Patrol.
    10-29-2015 - 2016 Grand Design 380TH. It's HUGE compared to a camper.
    10-19-2018 - traded truck for a 2016 Ram 3500 DRW Laramie CC 4 X 4 Long Box.
    03-16-2019 - Traded Momentum for a New 2018 374TH-R Solitude
    FULL TIME RV'er Nov 2021

  2. #22
    Site Sponsor
    Join Date
    Jul 2017
    Location
    SW Indiana
    Posts
    1,985
    Mentioned
    42 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MoonShadow_1911 View Post
    Interesting. I've got a bonded neutral plug on my Champion 3400 Dual Fuel inverter generator, and the Watchdog is just fine with it. Huh, thanks!

    Sent from my SM-N986U using Tapatalk
    The generator is upstream. If you were to plug another bonding plug into an outlet inside the RV, it would squawk.
    John & Kathy
    2014 F250 Lariat FX4 6.2L SBCC
    2014 Reflection 303RLS
    SW Indiana

  3. #23
    Long Hauler
    Join Date
    May 2020
    Location
    All over - Full-timing
    Posts
    2,557
    Mentioned
    46 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jkwilson View Post
    The generator is upstream. If you were to plug another bonding plug into an outlet inside the RV, it would squawk.
    Ah, got it! Thanks!

    Sent from my SM-N986U using Tapatalk
    Mark & Mary. Full-timing across the USA (and Canada)!
    Current Coach: 2021 Grand Design Reflection 320MKS
    Current Rig: 2019 Ford F350 SD Crew Cab, w/8' box, Lariat, SRW, 6.7l Diesel

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

DISCLAIMER:This website is not affiliated with or endorsed by Grand Design RV, LLC or any of its affiliates. This is an independent site.