Thread: Fuse size for Solar Controller
-
10-30-2022, 06:48 PM #11
- Join Date
- Jul 2017
- Location
- Jackson, MO
- Posts
- 529
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
Since the PV short circuit rating is 10amps I am wondering if the breaker should only be 10amps? I read on one of the question/answers on Amazon where the company said to be careful not to allow the circuit breaker to exceed the rating of the panels. The max power of the panel is 8.82amps.
DaleDale & Tammy
Retired U. S Army and Retired Helicopter Pilot
2021 Ford F-350, 6.7L Diesel, 4x4, Lariat Ultimate
2018 Grand Design Imagine 2670MK (sold)
2022 Grand Design Reflection 337RLS
-
10-30-2022, 07:09 PM #12
-
10-30-2022, 07:39 PM #13
-
10-31-2022, 08:55 AM #14
- Join Date
- Jul 2017
- Location
- Jackson, MO
- Posts
- 529
- Mentioned
- 1 Post(s)
- Tagged
- 0 Thread(s)
Bill,
A 15AMP circuit breaker will handle 180watts at 12 volts. Since the solar panel is 165watts, and I don't plan on adding anymore, I think I am going to add a 15AMP breaker on the supply as well as the battery line so I can completely shut off the electric to the controller. This is the one I think I am going to use https://www.amazon.com/gp/product/B0...35U6S8IT&psc=1
Thanks for the help and advice.
DaleLast edited by Dale G; 10-31-2022 at 06:03 PM.
Dale & Tammy
Retired U. S Army and Retired Helicopter Pilot
2021 Ford F-350, 6.7L Diesel, 4x4, Lariat Ultimate
2018 Grand Design Imagine 2670MK (sold)
2022 Grand Design Reflection 337RLS
-
10-31-2022, 07:26 PM #15
Sounds good! Good luck with it.
Bill2019 GMC 3500 SRW Sierra Denali Duramax