50-Amp RV Outlet Box With a Local Breaker

Thread Summary

Summarized on:
Original Member Title: 50 Amp Box Suggestions Needed
This AI-generated summary may contain inaccuracies. Please refer to the full thread for complete details.
A member building a new home wants a 50-amp-only RV receptacle box with a built-in breaker for a fifth wheel, with installation handled by the electrical contractor. Although the house panel already has a breaker, the member wants a local disconnect to avoid basement trips when connecting or disconnecting power; a separate 15-amp outlet is also planned nearby.

Several members favored a 50/30/20-amp combination panel for future flexibility and what they described as a small additional...
More...
I put a GE disconnect switch before the 50a power box so I have local cutoff. There is 60amp breaker on the panel in the basement. They do make this same switch with a breaker connection in the switch box. All of this is rated for external weather-rated install. Be aware that the current NEC requires a GFI breaker on RV power connection when installed in a residence, but a GFI breaker is not required for the same setups at RV Parks. I point this out because some RV electrical components cause GFI breakers to trip (hence the RV Park exception). And make sure your electrician knows the correct way to wire a NEMA 14-50R RV Receptacle.

​

 

Attachments

  • 20261010_181912.jpg
    20261010_181912.jpg
    93.1 KB · Views: 55
Last edited:
Not sure what type of EMS you have on your rig but make sure to verify the outlet is wired correctly.

Image 10-11-26 at 2.02 PM.png
 
And tell your electrician that its 50amp per leg. That will matter in the selection of wire gauge based on the distance between the RV outlet and your power panel. For me, the distance between the breaker panel and where my RV outlet was located required me to use 4.0 service entrance cable.
 
And tell your electrician that its 50amp per leg. That will matter in the selection of wire gauge based on the distance between the RV outlet and your power panel. For me, the distance between the breaker panel and where my RV outlet was located required me to use 4.0 service entrance cable.
did you mean #4 AWG or actually 4/0 ? If 4/0 that is a long way to the pedestal :)
 
@poohbear: 4/0. Electrical panel on one side of house, RV outlet on the other side of house and garage. Wire fed across basement, up garage wall, across 60' of garage ceiling and down to switch location. So yeah, a long expensive way to the pedestal.
 
I don't know why you would need a breaker in the panel. I have 14-50 receptacle on my shed and have plugged in 50A campers, 30A campers and 250A welders and have never tripped the breaker. Typically I only plug into a 20A receptacle with a 16 ga cord when it is at home unless someone is staying in the camper or we are working in there. You may be implying that you use the breaker as a switch which you SHOULD NOT DO. Breakers are overload protection only and NOT designed to function as a switch.
 
I don't know why you would need a breaker in the panel. I have 14-50 receptacle on my shed and have plugged in 50A campers, 30A campers and 250A welders and have never tripped the breaker. Typically I only plug into a 20A receptacle with a 16 ga cord when it is at home unless someone is staying in the camper or we are working in there. You may be implying that you use the breaker as a switch which you SHOULD NOT DO. Breakers are overload protection only and NOT designed to function as a switch.
Negative. A breaker is required by code and mine is installed in the home entry breaker panel. Switch is outside and is used to turn power on and off to the outlet - there is no breaker in my switch. There are similar switches that also have a beaker in the switch panel that can be used instead of a breaker in your home electrical panel. Also code - that pedestal breaker should be a GFCI breaker. But as I mentioned, that requirement is for residential installation where there is weather exposure (outside). RVs electrical components are notorious for leaking some current to ground, such as RV converters with RF filters. Leakage current is cumulative and enough current to ground (5mA) causes GFCI breakers to trip. This causes a lot of nuisance GFCI trips. By code, RV parks are not required to have GFCI breakers on their pedestals, but the NEC did not include that same exemption on residential RV pedestals.
 
Negative. A breaker is required by code and mine is installed in the home entry breaker panel. Switch is outside and is used to turn power on and off to the outlet - there is no breaker in my switch. There are similar switches that also have a beaker in the switch panel that can be used instead of a breaker in your home electrical panel. Also code - that pedestal breaker should be a GFCI breaker. But as I mentioned, that requirement is for residential installation where there is weather exposure (outside). RVs electrical components are notorious for leaking some current to ground, such as RV converters with RF filters. Leakage current is cumulative and enough current to ground (5mA) causes GFCI breakers to trip. This causes a lot of nuisance GFCI trips. By code, RV parks are not required to have GFCI breakers on their pedestals, but the NEC did not include that same exemption on residential RV pedestals.
Mine is actually a 50A welder receptacle that just happens to work with my 50A camper.
 
A 50A welder receptacle (NEMA 6-50R) uses two hot wires and one ground, it does not have a neutral wire that an RV receptacle (NEMA 14-50R) has.
Not all do - mine is a 14-50R in my garage (has 2 hots, a ground and a neutral) - most modern build houses runs a neutral for the 240V feeds (my dryer, hot tub and range receptacles all have neutrals) - I think they do this as these loads also have 120V electronics in them that will need the neutral to power up.
 
Then by definition it’s an RV receptacle, not a welder
I wired the 14-50R when I wanted an outdoor welder receptacle and long before I had an RV or my daughter needed to use it when she visited.
 