Hi Randy,
We have obviously travelled similar paths through balancing battery bank size, consumption rate and charging capacity.
I agree with what you say WRT maximum wire size and minimum length of run being very important.
I would add to this that quality of connectors and how they are crimped is equally important. Borrowing or buying a proper “battery lug” crimping tool is well worth it.
BTW, a good source for reasonably priced good quality heavy gauge wire and lugs is a welding supply store.
WRT battery capacity, the optimum range to discharge and recharge lead/acid batteries is between 50% and 80% state of charge.
Going below 50% risks permanent damage to the battery and going above 80% is great if you can get it, but takes an increasingly long time.
This is where a precision battery monitor becomes really useful. It can be programmed with the Ah capacity of the bank and will display state of charge as a %.
So, you know in the morning, what the bank is at (presumably between 50% and 80%) and how much you need to regain during the day.
Using your 450 Ah bank as an example, 80% is 360 Ah, 50% is 225 Ah . . . so you should ideally live within 135 Ah consumption and recharge per day.
A 450 watt solar array is going to be putting out a maximum of about 34 amps at an optimum 13.5 volts charging voltage.
The instantaneous rate of charge can be displayed on the monitor and will show how much of that theoretical 450 watts (34 amps) is actually going into the bank.
You will be able to see the effect of panel orientation to the sun, cloud cover, rate of charge acceptance by the batteries (goes down as bank % goes up), etc.
Then you can decide whether you really need to run the generator or the truck to catch up

.
Rob